To conduct load test on a dc shunt motor, it is coupled to a generator which is identical to the motor. The field of the generator is also connected to the same supply source as the motor. The armature of generator is connected to a load resistance. The armature resistance is 0.2 pu. Armature reaction and mechanical losses can be neglected. With rated voltage across the motor, the load resistance across the generator is adjusted to obtain rated armature current in both motor and generator. The pu value of this load resistance is | |
A. | 1 [Wrong Answer] |
B. | 0.98 [Wrong Answer] |
C. | 0.96 [Correct Answer] |
D. | 0.94 [Wrong Answer] |